0h2 fault in fuji FRENIC MEGA drive

1 Posts
1 Users
0 Reactions
13 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : External alarm comes when external fault at multi-function input terminal or faults comes from external control circuit.

0h2 fault in fuji FRENIC MEGA drive indicates External alarm. This means an external device tripped an alarm function or wiring is incorrect or multi-function contact input setting is incorrect.

  1. Remove the cause of the external fault and reset the fault.
  2. Properly connect the signal lines to the terminals assigned for external fault detection.
  3. Reconnect the signal line.
  4. Change the terminal settings.