E42.02 fault in inovance IS580 drive indicates CAN communication fault - "Commnunication gets interfered". This means the drive detects that the CAN bus communication is being interrupted or lost.
- Check if BUS wirings have loose connection or wrong connection.
- Check if BUS shielding is well connected, or if BUS cable is longer than limit.