E46.00 fault in inovance IS580 drive

1 Posts
1 Users
0 Reactions
19 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

E46.00 fault in inovance IS580 drive indicates "Pressure sensor is faulty". This means the drive has detected a problem with the pressure sensor input signal.

  • Check cables, connectors, and terminals for damage or looseness.
  • Ensure shielded cables are grounded properly to avoid noise.
  • Confirm that the pressure sensor receives the correct supply voltage (often 24V or specific analog voltage).
  • Measure the sensor output signal (usually analog voltage or current).