Forum

Share:
Notifications
Clear all

Err12 Input phase loss fault in inovance MD310 drive

1 Posts
1 Users
0 Reactions
70 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Input phase loss comes when input R,S,T have phase loss or imbalance. An Input Phase Loss "Err12" fault will occur when the DC bus ripple exceeds a pre-defined level. One (or more) of the input phases were lost.

"Err12" fault in inovance MD310 drive indicate "Input phase loss". This means one of the three input phases to the drive is disconnected or has a significant voltage drop.

  1. Large imbalance of voltage exists on the input of the drive.
  2. Drive is not properly sized for single phase input.
  3. Check input voltage.
  4. Check rectifier section using multimeter.
Share: