Err15 External fault in inovance MD290 drive

1 Posts
1 Users
0 Reactions
25 Views
Posts: 17563
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : External fault comes when external fault at multi-function input terminal or faults comes from external control circuit.

"Err15" fault in inovance MD290 drive indicate "External fault". This means a problem that is not directly related to the drive itself but rather an external issue triggering the fault condition.

Common Causes:

  1. Wiring Issues:

    • Loose or damaged cables connecting the drive to external devices can cause faults.
    • Check for short circuits, ground faults, or disconnected wires.
  2. External Equipment Faults:

    • Faults from connected motors, sensors, or other devices can trigger an external fault in the drive.
    • Inspect the external devices connected to the drive.
  3. Improper Configuration:

    • Incorrect parameter settings in the drive may cause the system to interpret external signals as faults.
    • Verify that all parameters related to external fault inputs are correctly configured.
  4. Noise Interference:

    • Electrical noise from nearby equipment can cause false triggering of external fault conditions.
    • Ensure proper grounding and shielding of cables and consider using filters if necessary.
  5. Faulty External Components:

    • Faulty external devices, such as relays, switches, or sensors, can send incorrect signals to the drive.
    • Test the components to ensure they are functioning correctly.

Troubleshooting Steps:

  1. Check the Fault Log:

    • Review the fault history on the drive’s display or software to identify the specific external fault that occurred.
  2. Inspect External Wiring:

    • Check all connections between the drive and external devices for any loose or damaged wires.
  3. Test External Devices:

    • Temporarily disconnect external devices to see if the fault clears. This can help isolate the faulty component.
  4. Review Drive Parameters:

    • Ensure that parameters related to external fault inputs are set correctly according to the system's requirements.
  5. Reduce Electrical Noise:

    • If noise interference is suspected, ensure that all cables are properly shielded and grounded. Consider using noise filters if necessary.