Inovance MD200, MD310 & MD290 Drive
351
Sep 07, 2024 7:20 am
Cause : Contactor faulty comes when the contactor is faulty. This can prevent the drive from starting or operating correctly.
"Err17" fault in inovance MD290 drive indicate "Contactor faulty". This means a problem with the contactor used to control the power supply to the drive.Â
Common Causes
- Contactor Failure: The contactor itself may have failed due to mechanical wear, electrical overload, or other issues.
- Connection Issues: Loose or corroded connections to the contactor can disrupt its function.
- Drive Internal Faults: A fault within the drive's internal circuitry can affect the contactor's operation.
Troubleshooting Steps
Inspect the Contactor:
- Visually inspect the contactor: Look for signs of physical damage, such as burns, pitting, or loose contacts.
- Test the contactor: Use a multimeter to measure the resistance between the contacts when the contactor is closed. The resistance should be very low.
- Replace the contactor if necessary: If the contactor is damaged or has high resistance, replace it with a new one of the correct specifications.
Check Connections:
- Inspect the connections: Ensure that the connections between the contactor and the drive, as well as the power supply, are tight and free of corrosion.
- Clean the connections if necessary: If the connections are dirty or corroded, clean them with a contact cleaner.
Verify Drive Internal Components:
- Check for internal faults: If the contactor appears to be functioning correctly, there might be a fault within the drive's internal circuitry.