Err55 Slave error in master-slave control fault in inovance MD290 drive

1 Posts
1 Users
0 Reactions
178 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Slave error in master-slave control comes when a problem with one or more of the slave drives. This can prevent the drives from operating in a synchronized mode, leading to reduced performance or instability.

"Err55" fault in inovance MD290 drive indicate "Slave error in master-slave control". This means a problems with the communication cable, connectors, or settings between the master and slave drives can cause synchronization errors.

Troubleshooting Steps

  1. Verify Communication:

    • Check cables and connections: Ensure that the communication cables between the master and slave drives are undamaged and securely connected.
    • Verify communication settings: Make sure that the communication settings (baud rate, parity, stop bits) are identical on all drives.
    • Test communication: Use a communication analyzer to verify that the drives can communicate with each other.
  2. Check Synchronization Settings:

    • Review synchronization parameters: Ensure that the synchronization parameters (e.g., speed reference, synchronization mode) are configured correctly on all drives.
    • Adjust settings if necessary: If the settings are incorrect, make the necessary adjustments to ensure proper synchronization.
  3. Inspect Slave Drive:

    • Check for hardware faults: Look for any signs of damage, overheating, or other issues with the slave drive.
    • Verify power supply: Ensure that the slave drive is receiving adequate power.
  4. Reduce Noise and Interference:

    • Identify noise sources: Look for any nearby electrical equipment or devices that might be generating noise or interference.
    • Shielding: If necessary, shield the communication cables or drives to reduce the impact of noise.
    • Grounding: Ensure proper grounding of all drives to minimize noise.