E16.12 fault in inovance MD800 drive

1 Posts
1 Users
0 Reactions
15 Views
Posts: 17564
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

"E16.12" fault in inovance MD800 drive indicate "the PDO mapping configured by CANopen is inconsistent with the actual communication mapping". This means the configured mapping doesn't align with the actual communication, it can lead to data transmission errors, synchronization issues, or device malfunctions.

Potential Causes:

  1. Incorrect PDO Configuration:
    • The PDO mapping settings in the drive's software might not match the actual requirements of the connected devices.
    • Incorrectly defined PDO objects, transmission types (TX/RX), or data lengths can cause mismatches.
  2. Device Misconfiguration:
    • The connected device might have a different PDO configuration than expected, leading to communication conflicts.
    • Ensure that both devices are configured to use the same PDO objects, transmission types, and data lengths.
  3. Network Issues:
    • Interference or noise on the CANopen bus can disrupt data transmission, leading to inconsistencies between the configured and actual mappings.
    • Check for physical damage to cables, faulty connectors, or other network problems.
  4. Software Bugs:
    • In rare cases, software bugs in the drive's firmware or the connected device's firmware can cause PDO mapping inconsistencies.

Troubleshooting Steps:

  1. Verify PDO Configuration:
    • Carefully review the PDO mapping settings in the drive's software.
    • Compare the configured PDO objects, transmission types, and data lengths with the expected values based on the connected device's specifications.
    • Ensure that the PDO mapping is consistent with the device's PDO configuration.
  2. Check Device Configuration:
    • If possible, access the configuration of the connected device and verify its PDO mapping settings.
    • Ensure that the device's PDO configuration matches the drive's settings.
  3. Test Communication:
    • Use a CANopen analyzer or monitoring tool to capture and analyze the CANopen communication traffic.
    • Compare the transmitted and received PDO data with the expected values based on the configured mapping.
    • Look for any discrepancies or errors in the data transmission.
  4. Check for Network Interference:
    • If you suspect network interference, try isolating the drive and the connected device to eliminate external factors.
    • Use shielded cables and proper grounding techniques to reduce noise.

 