E16.71 fault in inovance MD800 drive

1 Posts
1 Users
0 Reactions
17 Views
Posts: 17563
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

"E16.71" fault in inovance MD800 drive indicate the master station goes offline during operation of the communication card. When the master station goes offline during operation of an EtherCAT communication card, it can disrupt data transmission, synchronization, and the overall functionality of the network. This could be due to various factors, including:

  • Hardware Problems: Faulty master station, damaged cables, or incorrect connections.
  • Software Issues: Incorrect EtherCAT configuration, communication parameter mismatches, or software bugs.
  • Network Interference: Noise or interference on the EtherCAT bus.
  • Device Compatibility: Incompatibility between the master station and the EtherCAT card.

Troubleshooting Steps:

  1. Check Hardware:
    • Inspect the master station and the EtherCAT card for any physical damage or loose connections.
    • Verify that the cables connecting them are securely plugged in and that they are shielded to minimize interference.
    • Use a cable tester to check the integrity of the cables.
  2. Verify Software Configuration:
    • Ensure that the EtherCAT system parameters, including the master station address and communication settings, are configured correctly on both the master station and the EtherCAT card.
    • Check for any configuration errors or mismatches.
  3. Check for Network Interference:
    • If the EtherCAT bus is shared with other devices, try isolating the master station and the EtherCAT card to eliminate interference.
    • Use shielded cables and proper grounding techniques to reduce the susceptibility to noise.
  4. Test Device Compatibility:
    • If possible, try using a different master station or EtherCAT card to isolate the problem.