Err05 fault in inovance MD500 drive

1 Posts
1 Users
0 Reactions
290 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Over Voltage in Acceleration comes when the inverter's internal main circuit DC voltage to reach or exceed the specified value, the protection circuit is activated to stop the inverter output.

The circuit may also be activated by a surge voltage produced in the power supply system.

  1. Increase the acceleration time.
  2. Check the input power source.