Cause : Inverter overload comes when the output current has exceeded due to load too heavy or acceleration too fast. The "Err10" fault indicate that drive's output current has exceeded the drive's overload curve.

  1. Check the input power source.
  2. Select bigger capacity inverter.
  3. Increase the acceleration time.
  4. Avoid restarting when the motor is in rotation.