Calibrating a displacer level transmitter involves verifying its output signal response to changes in liquid level and adjusting it to match the desired measurement range. Here's a general procedure for calibrating a displacer level transmitter:
-
Gather Equipment:
- Obtain a reference measurement device such as a sight glass, dipstick, or another level transmitter with known accuracy.
- Ensure you have a pressure source or control valve to vary the liquid level in the vessel.
- Prepare a multimeter or loop calibrator to measure the output signal of the displacer level transmitter.
-
Isolate the Transmitter:
- Disconnect the displacer level transmitter from the process to avoid interference during calibration.
- Ensure that the liquid level in the vessel is stable and not subject to sudden changes during calibration.
-
Establish Calibration Points:
- Identify the desired calibration points, including the minimum and maximum levels to be measured by the displacer level transmitter.
- Use the reference measurement device to verify the actual liquid levels corresponding to these calibration points.
-
Apply Test Pressure:
- Adjust the liquid level in the vessel to the minimum calibration point.
- Measure the output signal of the displacer level transmitter at this level using the multimeter or loop calibrator.
- Record the measured output signal and the corresponding liquid level from the reference measurement device.
-
Adjust Zero Point:
- If necessary, adjust the zero point of the displacer level transmitter to match the measured output signal at the minimum calibration point.
- Some displacer level transmitters have zero adjustment screws or potentiometers that can be used to fine-tune the zero point. Follow the manufacturer's instructions for adjustment.
-
Apply Test Pressure for Span Calibration:
- Adjust the liquid level in the vessel to the maximum calibration point.
- Measure the output signal of the displacer level transmitter at this level using the multimeter or loop calibrator.
- Record the measured output signal and the corresponding liquid level from the reference measurement device.
-
Adjust Span:
- If necessary, adjust the span of the displacer level transmitter to match the measured output signal at the maximum calibration point.
- Some displacer level transmitters have span adjustment screws or potentiometers that can be used to adjust the span. Follow the manufacturer's instructions for adjustment.
-
Verify Calibration:
- After adjusting the zero and span, repeat the calibration process to verify that the displacer level transmitter accurately measures the liquid level within the desired range.
- Ensure the output signal of the transmitter corresponds correctly to changes in liquid level.
-
Finalize Calibration:
- Once satisfied with the calibration results, finalize the process by documenting the calibration procedure, including the calibration points, measured output signals, adjustments made, and any observed deviations.
- Label the displacer level transmitter with the calibration date and any relevant information.
- Reconnect the transmitter to the process and ensure it operates correctly under normal conditions.
-
Regular Maintenance:
- Schedule regular inspections and calibrations of the displacer level transmitter to ensure continued accuracy and reliability.
- Monitor the performance of the transmitter over time and recalibrate as necessary to maintain proper operation.
By following these steps, you can effectively calibrate a displacer level transmitter to ensure accurate and reliable level measurement in your process or application. If you're unsure about any steps or require assistance, consider consulting the transmitter manufacturer or a professional calibration service.