/P Converter calibration
Calibrating an I/P converter, which stands for "Current to Pressure Converter," involves ensuring that the output pressure accurately corresponds to the input electrical current signal within a specified range. Here's a general procedure for calibrating an I/P converter:
  1. Prepare Equipment:
    • Gather a reference pressure gauge or calibrator capable of generating the desired pressure range for calibration.
    • Ensure you have a power supply to provide the input electrical current signal to the I/P converter.
    • Prepare a multimeter or pressure calibrator to measure the output pressure of the I/P converter.
  2. Isolate the I/P Converter:
    • Disconnect the I/P converter from the process to avoid interference during calibration.
    • Ensure that the power supply is connected securely to provide the input electrical current signal and the output pressure port is connected to the pressure gauge or calibrator.
  3. Establish Calibration Points:
    • Identify the desired calibration points, including the minimum and maximum pressures to be generated by the I/P converter.
    • Use the reference pressure gauge or calibrator to verify the actual pressure levels corresponding to these calibration points.
  4. Apply Input Current Signal:
    • Set the power supply to provide the minimum input current signal required by the I/P converter.
    • Measure the output pressure of the I/P converter using the pressure gauge or calibrator and record the reading.
    • Verify that the output pressure corresponds correctly to the input current signal at this calibration point.
  5. Adjust Zero Point:
    • If the output pressure does not match the expected value at the minimum calibration point, adjust the zero point of the I/P converter as needed.
    • Some I/P converters have zero adjustment screws or potentiometers that can be used to adjust the zero point. Follow the manufacturer's instructions for adjustment.
    • Incrementally adjust the zero point and repeat the calibration process until the output pressure matches the expected value at the minimum calibration point.
  6. Apply Input Current Signal for Span Calibration:
    • Set the power supply to provide the maximum input current signal required by the I/P converter.
  7. Adjust Span:
    • If the output pressure does not match the expected value at the maximum calibration point, adjust the span of the I/P converter as needed.
    • Some I/P converters have span adjustment screws or potentiometers that can be used to adjust the span. Follow the manufacturer's instructions for adjustment.
    • Incrementally adjust the span and repeat the calibration process until the output pressure matches the expected value at the maximum calibration point.
  8. Verify Calibration:
    • After adjusting the zero and span, repeat the calibration process to verify that the I/P converter accurately generates the output pressure within the desired range.
    • Ensure the output pressure of the I/P converter corresponds correctly to the input current signal.
  9. Finalize Calibration:
    • Once satisfied with the calibration results, finalize the process by documenting the calibration procedure, including the calibration points, measured output pressures, adjustments made, and any observed deviations.
    • Label the I/P converter with the calibration date and any relevant information.
    • Reconnect the I/P converter to the process and ensure it operates correctly under normal conditions.
  10. Regular Maintenance:
    • Schedule regular inspections and calibrations of the I/P converter to ensure continued accuracy and reliability.
    • Monitor the performance of the converter over time and recalibrate as necessary to maintain proper operation.
By following these steps, you can effectively calibrate an I/P converter to ensure accurate and reliable pressure output in your process or application. If you're unsure about any steps or require assistance, consider consulting the converter manufacturer or a professional calibration service.