Calibrating an I/P converter, which stands for "Current to Pressure Converter," involves ensuring that the output pressure accurately corresponds to the input electrical current signal within a specified range. Here's a general procedure for calibrating an I/P converter:
-
Prepare Equipment:
- Gather a reference pressure gauge or calibrator capable of generating the desired pressure range for calibration.
- Ensure you have a power supply to provide the input electrical current signal to the I/P converter.
- Prepare a multimeter or pressure calibrator to measure the output pressure of the I/P converter.
-
Isolate the I/P Converter:
- Disconnect the I/P converter from the process to avoid interference during calibration.
- Ensure that the power supply is connected securely to provide the input electrical current signal and the output pressure port is connected to the pressure gauge or calibrator.
-
Establish Calibration Points:
- Identify the desired calibration points, including the minimum and maximum pressures to be generated by the I/P converter.
- Use the reference pressure gauge or calibrator to verify the actual pressure levels corresponding to these calibration points.
-
Apply Input Current Signal:
- Set the power supply to provide the minimum input current signal required by the I/P converter.
- Measure the output pressure of the I/P converter using the pressure gauge or calibrator and record the reading.
- Verify that the output pressure corresponds correctly to the input current signal at this calibration point.
-
Adjust Zero Point:
- If the output pressure does not match the expected value at the minimum calibration point, adjust the zero point of the I/P converter as needed.
- Some I/P converters have zero adjustment screws or potentiometers that can be used to adjust the zero point. Follow the manufacturer's instructions for adjustment.
- Incrementally adjust the zero point and repeat the calibration process until the output pressure matches the expected value at the minimum calibration point.
-
Apply Input Current Signal for Span Calibration:
- Set the power supply to provide the maximum input current signal required by the I/P converter.
- Measure the output pressure of the I/P converter using the pressure gauge or calibrator and record the reading.
- Verify that the output pressure corresponds correctly to the input current signal at this calibration point.
-
Adjust Span:
- If the output pressure does not match the expected value at the maximum calibration point, adjust the span of the I/P converter as needed.
- Some I/P converters have span adjustment screws or potentiometers that can be used to adjust the span. Follow the manufacturer's instructions for adjustment.
- Incrementally adjust the span and repeat the calibration process until the output pressure matches the expected value at the maximum calibration point.
-
Verify Calibration:
- After adjusting the zero and span, repeat the calibration process to verify that the I/P converter accurately generates the output pressure within the desired range.
- Ensure the output pressure of the I/P converter corresponds correctly to the input current signal.
-
Finalize Calibration:
- Once satisfied with the calibration results, finalize the process by documenting the calibration procedure, including the calibration points, measured output pressures, adjustments made, and any observed deviations.
- Label the I/P converter with the calibration date and any relevant information.
- Reconnect the I/P converter to the process and ensure it operates correctly under normal conditions.
-
Regular Maintenance:
- Schedule regular inspections and calibrations of the I/P converter to ensure continued accuracy and reliability.
- Monitor the performance of the converter over time and recalibrate as necessary to maintain proper operation.
By following these steps, you can effectively calibrate an I/P converter to ensure accurate and reliable pressure output in your process or application. If you're unsure about any steps or require assistance, consider consulting the converter manufacturer or a professional calibration service.