"Pressure switch calibration" is a critical process to ensure the accurate operation of pressure switches in various industrial applications. These switches play a crucial role in monitoring and controlling pressure-related processes. Let’s dive into the procedure for calibrating pressure switches:
Pressure Switch Calibration Procedure
Understanding Pressure Switch Basics
Before we proceed with calibration, let’s review some essential terms related to pressure switches:
- Set Point:
- The pressure at which the switch changes state (opens or closes).
- Normal State:
- The switch state when at barometric pressure or the ideal state (either OPEN or CLOSED, depending on the switch type).
- Reset Pressure:
- The pressure at which the switch resets back to the normal state.
- Tolerance:
- The allowable variation from the set point pressure.
- Repeatability:
- The closeness of agreement between consecutive measurements.
- Dead Band:
- The pressure difference between the change-of-states (e.g., OPEN to CLOSE or CLOSE to OPEN).
- Trip Type:
- The direction in which the change-of-state occurs.
- If the trip type is low, the change-of-state happens when the pressure is falling.
- If the trip type is high, the change-of-state happens when the pressure is rising.
- The direction in which the change-of-state occurs.
Calibration Steps:
- Depressurize and Isolate:
- Ensure the pressure switch is depressurized and isolated from the process.
- Connect Pressure Source and Calibrator:
- Connect the pressure source (preferably a hand pump) and the pressure calibrator (pressure gauge) to the pressure switch input.
- Check Electrical Output:
- Use a multimeter in continuity mode to verify the switch contacts:
- For a normally open (NO) switch, check that the contacts are open.
- For a normally closed (NC) switch, check that the contacts are closed.
- Use a multimeter in continuity mode to verify the switch contacts:
- Test Set Point:
- Apply pressure to the switch until it changes state (e.g., from OPEN to CLOSE for an NO switch).
- Record the pressure at which the switch changes state (set point).
- Test Reset Pressure:
- Release pressure until the switch resets back to the normal state (e.g., from CLOSE to OPEN for an NO switch).
- Record the reset pressure.
- Repeat for Repeatability:
- Repeat the test at least once to determine repeatability.