OC3 fault in INVT GD10 drive

1 Posts
1 Users
0 Reactions
70 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

OC3 fault in INVT GD10 drive indicates an overcurrent fault during constant speed operation. This means the motor is drawing more current than the drive can handle while running at a steady speed.

Common Causes:

  1. Mechanical Overload: The motor may be overloaded due to excessive mechanical load or friction.
  2. Incorrect Motor Parameter Settings: If the motor parameters are not configured correctly, the drive may miscalculate the required current.
  3. Power Supply Issues: Insufficient power supply or voltage fluctuations can also trigger the OC3 fault.
  4. Internal Drive Faults: In rare cases, internal faults within the drive itself can trigger the OC3 fault.

Troubleshooting Steps:

  1. Check Mechanical Load:
    • Ensure that the motor shaft rotates freely and there are no mechanical obstructions.
    • Check for any binding or excessive friction in the mechanical system.
  2. Verify Motor Parameters:
    • Ensure that the motor's rated power, voltage, and current are correctly entered in the drive's parameter settings.
    • Consult the motor's nameplate for accurate values.
  3. Check Power Supply:
    • Verify that the power supply voltage and current are within the specified range.
    • Ensure that the power supply is capable of delivering the required power to the drive.
  4. Check for Internal Faults:
    • If the above steps do not resolve the issue, it may be necessary to inspect the drive's internal components.