OL3 fault in invt gd10 drive
OL3 fault in an INVT GD10 drive indicates an Electrical Overload Pre-Alarm. This means the inverter's output current has approached a pre-set overload threshold, but hasn't yet exceeded it. This is often a precursor to a full-blown overload (OL1 or OL2) if the condition persists.
Common Causes of OL3 Faults:
  1. Mechanical Overload:
    • Excessive Load: The motor may be subjected to a load that is nearing its rated capacity.
    • Mechanical Issues: Mechanical problems like bearing wear, belt slippage, or pump blockages can increase the motor's load.
  2. Electrical Overload:
    • Voltage Fluctuations: Variations in the supply voltage can lead to increased motor current draw.
    • Short Circuits: Internal or external short circuits can cause excessive current flow.
    • Incorrect Motor Sizing: The motor may be undersized for the application.
  3. Inverter Settings:
    • Incorrect Current Limit: The inverter's current limit may be set too low, causing frequent pre-alarm conditions.
    • Motor Parameter Mismatch: Incorrect motor parameters can lead to inaccurate current calculations.
  1. Check the Mechanical Load:
    • Inspect the driven equipment for any signs of mechanical issues.
    • Ensure the load is within the motor's rated capacity.
  2. Verify Electrical Connections:
    • Check for loose or damaged connections in the motor and inverter wiring.
    • Inspect the motor windings for signs of damage or overheating.
  3. Inspect the Inverter:
    • Verify the inverter's current limit setting and adjust it if necessary.
    • Ensure the motor parameters are correctly configured in the inverter.
  4. Monitor Motor Temperature:
    • Use a thermal imaging camera or a contact thermometer to measure the motor's temperature.
    • Excessive temperature can indicate an impending overload.