LS L100, S100, iG5A & iV5L Drive
1
Posts
1
Users
0
Reactions
326
Views
Apr 13, 2024 10:49 am
Cause : Overload trip comes when the inverter turns off its output if the output current of the inverter flows at 150% of the inverter rated current for more than the current limit time (1 min).
- Load is greater than the inverter rating.
- Upgrade the capacity of motor and inverter or reduce the load weight.
- Torque boost scale is set too large.
- Reduce torque boost scale.