EtA fault in L&T CX2000 drive

1 Posts
1 Users
0 Reactions
154 Views
Posts: 18018
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Contract A Fault signal comes when multi-function input terminal (I17-I24) is set to 18 {External fault signal input: A (Normal Open Contact)}, the inverter turns off the output.

"EtA" fault indicate an external device tripped an alarm function or wiring is incorrect or multi-function contact input setting is incorrect.

  1. The terminal set to “18 (External fault- A)” or “19 (External fault-B)” in I20-I24 in I/O group is ON.
  2. Eliminate the cause of fault at circuit connected to external fault terminal or cause of external fault input.