F0004 Inverter overtemperature fault in siemens micromaster 420 or MM420 drive - comes when ambient temperature is too high or IGBT is overload or cooling fan is faulty.

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause - comes when ambient temperature is too high or IGBT is overload or cooling fan is faulty.

1. inadequate cooling

2. ambient temperature is too high.

Diagnosis & Remedy please check the following:

1. is the pulse frequency P1800 set to the factory setting ? If required reset P1800.

2. does the ambient temperature lie within the permissible limits ?

3. reduce the load and / or ensure adequate cooling.

4. The fan rotate if the inverter is operational