F0041 fault in siemens micromaster 420 or MM420 drive - comes when motor data identification run unsuccessful due to load missing or current limit value reached during identification.
F0041 Failure, motor data identification fault in siemens micromaster 420 or MM420 drive
Cause
Motor data identification run unsuccessful (refer to fault value r0949):
- r0949 = 0: Load missing.
- r0949 = 1: Current limit value reached during identification.
- r0949 = 2: Identified stator resistance less than 0.1% or greater than 100%.
- r0949 = 30: Current controller at voltage limit value
- r0949 = 40: Identified data set inconsistent; at least one identification run unsuccessful
Diagnosis & Remedy
Please check the following:
- r0949 = 0: Is the motor connected to the inverter ?
- r0949 = 1-40: Is the motor data in P0304-P0311 correct ?
- r0949 = 1-40: Motor circuit configuration correct (star, delta configuration)
1. Check motor data
2. Check loading on motor
3. Boost settings too high (P1310,P1311, P1312)
4. Check parameter for motor thermal time constant
5. Check parameter for motor I2t warning level