F0450 fault in siemens micromaster 420 or MM420 drive

2 Posts
1 Users
0 Reactions
278 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

F0450 fault in siemens micromaster 420 or MM420 drive -  comes when self-test routine unsuccessful or failure of the internal RAM at the switch-on test.

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Failure BIST tests.

Self-test routine unsuccessful (refer to fault value r0949):
- r0949 = 1: Self-test routine for power module components unsuccessful
- r0949 = 2: Self-test routine for closed-loop control module components unsuccessful
- r0949 = 4: Several function tests were unsuccessful
- r0949 = 8: Several tests carried-out at the I/O module were unsuccessful (only MICROMASTER 420)
- r0949 = 16: Failure of the internal RAM at the switch-on test

Diagnosis & Remedy

- the drive is functional, but several functions are not correctly executed.
- replace the drive