Forum

Share:
Notifications
Clear all

A0501 alarm in siemens micromaster 430 or MM430 drive

2 Posts
1 Users
0 Reactions
195 Views
Posts: 14965
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem A0501 alarm in siemens micromaster 430 or MM430 drive ?

1 Reply
Posts: 14965
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Current Limit. Motor power (P0307) does not correspond to the inverter power (P0206). Motor leads are too long. Earth faults.

Diagnose & Remedy

Check the following:
1. Motor power (P0307) must correspond to inverter power (r0206)
2. Cable length limits must not be exceeded
3. Motor cable and motor must have no short-circuits or earth faults
4. Motor parameters must match the motor in use
5. Value of stator resistance (P0350) must be correct
6. Motor must not be obstructed or overloaded
- Increase the ramp-up-time.
- Reduce the boost level (V/f control: P1311 & P1312)

Reply
Share: