Forum

Share:
Notifications
Clear all

A0503 alarm in siemens micromaster 430 or MM430 drive

2 Posts
1 Users
0 Reactions
379 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A0503 alarm in siemens micromaster 430 or MM430 drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : UnderVoltage Limit. Main supply failed. Main supply (P0210) and consequently DC-link voltage (r0026) below specified limit (P2172).

Diagnose & Remedy\

1. Supply voltage (P0210) must lie within limits indicated on rating plate
2. Supply must not be susceptible to temporary failures or voltage reductions
3. Enable kinetic buffering (P1240 = 2)

Reply
Share: