A0505 alarm in siemens micromaster 430 or MM430 drive

2 Posts
1 Users
0 Reactions
308 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A0505 alarm in siemens micromaster 430 or MM430 drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Inverter I2t. Warning level (P0294) exceeded, output frequency and/or pulse frequency will be reduced if parameterized (P0290).

Diagnose & Remedy

Check the following:
1. Load duty cycle must lie within specified limits
2. Motor power (P0307) must match inverter power (r0206)