Forum

Share:
Notifications
Clear all

F0002 OverVoltage fault in siemens micromaster 430 or MM430 drive

2 Posts
1 Users
0 Likes
585 Views
Posts: 14958
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem F0002 Over Voltage fault in siemens micromaster 430 or MM430 drive ?

1 Reply
Posts: 14958
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Over Voltage .

- DC-link controller disabled (P1240 = 0)

- DC-link voltage (r0026) exceeds trip level (P2172)

- Overvoltage can be caused either by too high main supply voltage or if motor is in regenerative mode. Regenerative mode can be caused by fast ramp downs or if the motor is driven from an active load.

Diagnose & Remedy

Check the following:

1. Supply voltage (P0210) must lie within limits indicated on rating plate
2. DC-link voltage controller must be enabled (P1240) and parameterized properly
3. Ramp-down time (P1121) must match inertia of load
4. Required braking power must lie within specified limits

Reply
Share: