How can resolve problem A0511 alarm in siemens micromaster 440 or MM440 drive ?
Cause : Motor Over Temperature - Motor overloaded, Load duty cycle too high.
Diagnosis & Remedy
Independently of the kind of temperature determination check:
- P0604 motor temperature warning threshold
- P0625 motor ambient temperature
- If (P0601 = 0 or 1) Check the following:
1. Check if name plate data are correct (if not perform quick commissioning)
2. Accurate equivalent circuit data can be found by performing motor identification (P1910=1).
3. Check if motor weight (P0344) is reasonable. Change if necessary.
4. Via P0626, P0627, P0628 the standard over temperatures can be changed, if the motor is not a Siemens standard motor.
- If (P601 = 2) Check the following:
1. Check if temperature shown in r0035 is reasonable.
2. Check if the sensor is a KTY84 (other sensors are not supported)