A0590 alarm in siemens micromaster 440 or MM440 drive

2 Posts
1 Users
0 Likes
196 Views
Posts: 14784
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem A0590 alarm in siemens micromaster 440 or MM440 drive ?

1 Reply
Posts: 14784
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

 Cause : Encoder feedback loss warning - Signal from Encoder lost; Inverter might have switched to sensorless vector control(check also alarm value r0949):

Diagnosis & Remedy Stop inverter and then
- Check encoder fitted. If encoder fitted and r0949 = 5, select encoder type via P0400.
- If encoder fitted and r0949 = 6, check connections between encoder module and inverter.
- If encoder not fitted and r0949 = 5, select SLVC mode (P1300 = 20 or 22).
- If encoder not fitted and r0949 = 6, set P0400 = 0.
- Check connections between encoder and inverter
- Check that encoder not faulty (select P1300 = 0, run at fixed speed, check encoder feedback signal in
r0061)
- Increase encoder loss threshold in P0492