How can resolve problem A0910 alarm in siemens micromaster 440 or MM440 drive ?

1 Reply
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Vdc-max controller de-activated - Vdc max controller has been de-activated, since controller is not capable of keeping DC-link voltage (r0026) within limits (refer to r0026 and P1240).

- Occurs if main supply voltage (P0210) is permanently too high.
- Occurs if motor is driven by an active load, causing motor to goes into regenerative mode.
- Occurs at very high load inertias, when ramping down.

Diagnosis & Remedy

Check the following:
- Input voltage (P0210) must lie within range.
- Load must be match.