Forum

Share:
Notifications
Clear all

A0912 alarm in siemens micromaster 440 or MM440 drive

2 Posts
1 Users
0 Likes
291 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem A0912 alarm in siemens micromaster 440 or MM440 drive ?

1 Reply
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Vdc-min controller active

- Vdc min controller will be activated if DC-link voltage (r0026) falls below minimum level (refer to r0026
and P1240).
- The kinetic energy of the motor is used to buffer the DC-link voltage, thus causing deceleration of the
drive!
- So short mains failures do not necessarily lead to an undervoltage trip.

Reply
Share: