F0004 fault in siemens micromaster 440 or MM440 drive

2 Posts
1 Users
0 Likes
417 Views
Posts: 14958
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem F0004 fault in siemens micromaster 440 or MM440 drive ?

1 Reply
Posts: 14958
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Inverter Over Temperature.

- Ventilation inadequate
- Ambient temperature is too high.
- Actual drive converter temperature r0037 exceeds the overtemperature threshold (refer to P0292)

Diagnosis & Remedy

Check the following:
- Fan must turn when inverter is running
- Pulse frequency must be set to default value
- Ambient temperature could be higher than specified for the inverter
- Reduce the load and / or ensure adequate cooling

Additional meaning for frame sizes FX and GX:
- P949 = 1: Rectifier overtemperature
- P949 = 2: Ambient overtemperature
- P949 = 3: EBOX overtemperature

Reply