Cause : Inverter temp. signal lost comes when the drive cannot read the temperature of the heatsink, which is a critical component for preventing overheating.
The F0012 fault in Siemens Micromaster 440 indicates a inverter temperature sensor issue. This means the drive cannot detect the temperature of the heatsink.
Here are some steps to diagnose and potentially resolve the issue:
-
Check Connections:
- Ensure all electrical connections to the temperature sensor are secure and properly connected.
- Inspect for any loose or damaged wires.
-
Inspect the Temperature Sensor:
- Verify that the temperature sensor is functioning correctly.
- If possible, test the sensor with a multimeter to check for correct resistance values according to the sensor's specifications.
-
Verify Parameter Settings:
- Check the parameter settings in the inverter's configuration. Ensure that the parameters related to the temperature sensor are correctly set.
-
Check for Overheating:
- Ensure that the inverter is not overheating due to external factors such as a blocked cooling fan or high ambient temperatures.
- Clean any dust or debris from the cooling fins and ensure proper ventilation.
-
Reset the Fault:
- Attempt to reset the fault by turning off the inverter and turning it back on. Sometimes, a temporary glitch can cause such faults.