Cause : Mains Phase Missing comes when one or more of the mains input phases is missing or has a significant voltage imbalance.
The F0020 fault in Siemens Micromaster 440 indicates a missing phase from the supply voltage. This means the drive isn't detecting all three phases of the incoming power supply.
Here are some steps to diagnose and resolve this issue:
  1. Check Mains Supply:
    • Verify that the incoming mains supply is present on all phases (L1, L2, and L3).
    • Use a multimeter to measure the voltage between phases to ensure they are within the specified range.
  2. Inspect Connections:
    • Ensure that all power connections are secure and properly tightened.
    • Check for any signs of loose connections, damaged cables, or burned terminals.
  3. Check Input Fuses/Breakers:
    • Verify that all input fuses or circuit breakers are intact and not tripped.
    • Replace any blown fuses or reset tripped breakers as necessary.
  4. Measure Voltage Balance:
    • Confirm that the voltage levels between the phases are balanced. A significant imbalance can trigger this fault.
    • The voltage difference between phases should be minimal.
  5. Inspect Supply Quality:
    • Check the quality of the mains supply. Ensure there are no significant fluctuations or drops in voltage.
    • Investigate any potential sources of electrical noise or interference that could affect the inverter.