Cause : Communication fault (inverter) comes when the inverter trips when communication error occurs consecutively for the permissible number of retries or more when Pr.335 RS-485 communication retry count "9999" during RS-485 communication from the RS-485 terminals. The inverter also trips if communication is broken for the period of time set in Pr.336 RS-485 communication check time interval.
  1. Check the RS-485 terminal wiring.
  2. Perform wiring of the RS-485 terminals properly.