Cause : Inverter overload trip comes when the temperature of the output transistor element exceeds the protection level while a current flows at the rated output current level or higher without causing an overcurrent trip, the inverter output is stopped.
- Check that acceleration/deceleration time is not too short.
- Check that torque boost setting is not too large (small).
- Check that load pattern selection setting is appropriate for the load pattern of the using machine.
- Check the motor for the use under overload.
- Set the acceleration/deceleration time longer.
- Adjust the torque boost setting.
- Set the load pattern selection setting according to the load pattern of the using machine.