Cause : Model error comes when a different model was used when parameter copy from the operation panel or parameter verification was performed.
- The data in the operation panel were not correct when parameter copy from the operation panel or parameter verification was performed.
- Check that the parameter copy or verification source inverter is of the same model.
- Check that parameter copy to the operation panel was not interrupted by switching OFF the power or by disconnecting the operation panel.
- Perform parameter copy and parameter verification between inverters of the same model (FR-A700 series).
- Perform parameter copy to the operation panel from the inverter again.