E.AIE fault error code in Mitsubishi D700 drive

1 Posts
1 Users
0 Reactions
786 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Analog input fault comes when the inverter output is shut off when a 30 mA or higher current or a 7.5 V or higher voltage is input to terminal 2 while the current input is selected by Pr.73 Analog input selection, or to terminal 4 while the current input is selected by Pr.267 Terminal 4 input selection.

  1. Check the Pr.73, Pr.267, and the voltage/current input switch settings.
  2. Either give a current less than 30 mA, or set Pr.73, Pr.267, and the voltage/current input switch to the voltage input and input a voltage.