Cause : Inrush current limit circuit fault comes when the converter operation when the inrush current limit contactor does not turn ON, or a thermostat of the limit resistor activates.

  1. The converter output is shut off when the inrush current limit circuit is damaged.
  2. Check that frequent power ON/OFF is not repeated.
  3. Configure a circuit where frequent power ON/OFF is not repeated.