E.OC1 fault error code in Mitsubishi D700 drive

1 Posts
1 Users
0 Reactions
1,306 Views
Posts: 18163
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Overcurrent trip during acceleration comes when the inverter output current reaches or exceeds approximately 200% of the rated current during acceleration, the protective circuit is activated and the inverter trips.

  1. Check for sudden speed acceleration.
  2. Check if the downward acceleration time is too long in a lift application.
  3. Check for output short-circuit.
  4. Check that the Pr.3 Base frequency setting is not 60 Hz when the motor rated frequency is 50 Hz.
  5. Check if the stall prevention operation level is set too high. Check if the fast-response current limit operation is disabled.
  6. Check that the regenerative driving is not performed frequently. (Check if the output voltage becomes larger than the V/F reference voltage at regenerative driving and overcurrent occurs due to increase in the motor current.)
  7.  
  8. Check that the encoder wiring and the specifications are correct.
  9. Check also that the motor wiring (U, V, W) is correct (under vector control).
  10. Check that the rotation direction is not switched from forward to reverse rotation (or from reverse to forward) during torque control under Real sensorless vector control.
  11. Check that the inverter capacity matches with the motor capacity.
  12. Check if a start command is given to the inverter while the motor is coasting.