E.OC2 fault error code in Mitsubishi D700 drive

1 Posts
1 Users
0 Reactions
1,034 Views
Posts: 18163
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Overcurrent trip during constant speed comes when the inverter output current reaches or exceeds approximately 200% of the rated current during constant speed operation, the protective circuit is activated and the inverter trips.

  1. Check for sudden load change.
  2. Check for output short-circuit.
  3. Check if the stall prevention operation level is set too high. Check if the fast-response current limit operation is disabled.
  4. Check that the rotation direction is not switched from forward to reverse rotation (or from reverse to forward) during torque control under Real sensorless vector control.
  5. Check that the inverter capacity matches with the motor capacity.
  6. Check if a start command is given to the inverter while the motor is coasting.