Cause : Regenerative overvoltage trip during acceleration comes when the inverter's internal main circuit DC voltage to reach or exceed the specified value, the protection circuit is activated to stop the inverter output. The circuit may also be activated by a surge voltage produced in the power supply system.
- Check for too slow acceleration. (e.g. during downward acceleration in vertical lift load)
- Check that the Pr.22 Stall prevention operation level is not set to the no load current or lower.
- Check if the stall prevention operation is frequently activated in an application with a large load inertia.
- Set the acceleration time shorter.
- Set a value larger than the no load current in Pr.22.