IH fault error code in Mitsubishi CS80 drive

1 Posts
1 Users
0 Reactions
230 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Inrush current limit resistor overheat comes when the inrush current limit resistor is a PTC thermistor. Resistance of the PTC thermistor is increased when power ON/OFF is repeated.

When the resistance is increased, a huge gap between the peak voltage and the bus voltage is generated and the gap may cause a large inrush current flow. The surge voltage causes overvoltage error and the inverter displays a warning indication.

  1. Check that power ON/OFF is not repeated frequently.
  2. Check that the inrush current limit circuit is not damaged.
  3. Configure a circuit where frequent power ON/OFF is not repeated.