Cause : Converter operation disabled comes when the regenerative operation is not possible due to data processing in the converter such as during operation triggered by the SOF signal.
- Check that the SOF signal is not ON.
- Check that the multifunction regeneration converter was reset after Parameter copy.
- Check if the converter is attempted to be run with power supplied not to the main circuit but to the control circuit.
- Check that the power supply condition is stable.