Forum

Share:
Notifications
Clear all

OL fault error code in Mitsubishi D700 drive

1 Posts
1 Users
0 Reactions
174 Views
Posts: 17563
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Stall prevention (overcurrent) comes when the output current of the inverter exceeds the stall prevention operation level (Pr. 22 Stall prevention operation level, etc.), this function stops the increase in frequency until the overload current decreases to prevent the inverter from resulting in overcurrent trip. When the overload current has reduced below stall prevention operation level, this function increases the frequency again.

  1. When the output current of the inverter exceeds the stall prevention operation level (Pr. 22 Stall prevention operation level, etc.), this function reduces frequency until the overload current decreases to prevent the inverter from resulting in overcurrent trip. When the overload current has reduced below stall prevention operation level, this function increases the frequency up to the set value.
  2. When the output current of the inverter exceeds the stall prevention operation level (Pr. 22 Stall prevention operation level, etc.), this function stops the decrease in frequency until the overload current decreases to prevent the inverter from resulting in overcurrent trip. When the overload current has decreased below stall prevention operation level, this function decreases the frequency again.
  3. Check that the Pr. 0 Torque boost setting is not too large.
  4. Check that the Pr. 7 Acceleration time and Pr. 8 Deceleration time settings are not too small.
  5. Check that the load is not too heavy.
Share: