UV fault error code in Mitsubishi E700 drive

1 Posts
1 Users
0 Reactions
519 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Undervoltage comes when the power supply voltage of the inverter decreases, the control circuit will not perform normal functions. In addition, the motor torque will be insufficient and/or heat generation will increase. To prevent this, if the power supply voltage decreases below about 115VAC (about 230VAC for 400V class), this function stops the inverter output and displays UV.

  1. An alarm is reset when the voltage returns to normal.
  2. Check that the power supply voltage is normal.
  3. Check the power supply system equipment such as power supply.