If the power supply voltage of the inverter decreases, the control circuit will not perform normal functions. In addition, the motor torque will be insufficient and/or heat generation will increase.
- To prevent this, if the power supply voltage decreases to about 115 VAC (230 VAC for the 400 V class, 330 VAC for the 575 V class, 58 VAC for the 100 V class) or below (when the PM sensorless vector control is selected: about 156 VAC (311 VAC for the 400 V class, 448 VAC for the 575 V class, 78 VAC for the 100 V class) or below), this function shuts off the inverter output and "UV" is displayed.
- The warning is removed when the voltage returns to normal.
- Check that the power supply voltage is normal.
- Check the devices on the power system such as the power supply itself.