Mitsubishi FR-F Series- FR-F800, FR-F800-E, FR-F846-E2 & FR-F700 Drive
1
Posts
1
Users
0
Reactions
157
Views
Apr 02, 2024 4:45 am
Cause : Inrush current limit circuit fault comes when the inverter trips when the resistor of the inrush current limit circuit is overheated. The inrush current limit circuit failure.
- Check that frequent power ON/OFF is not repeated.
- Check that no meltdown is found in the primary side fuse (5A) in the power supply circuit of the
inrush current suppression circuit contactor (FR-F740-132K or more) or no fault is found in the power supply circuit of the contactor. - Check that the power supply circuit of inrush current limit circuit contactor is not damaged.