590
Apr 01, 2024 10:12 am
Cause : Overcurrent trip during deceleration or stop comes when the inverter output current reaches or exceeds approximately 170% of the rated inverter current during deceleration (other than acceleration or constant speed), the protective circuit is activated to stop the inverter output.
- Check for sudden speed reduction.
- Check for output short-circuit.
- Check for too fast operation of the motor's mechanical brake.
- Check if the stall prevention operation level is set too high. Check if the fast-response current limit operation is disabled.
- Check that the power supply for RS-485 terminal is not shorted .
- Check that the rotation direction is not switched from forward to reverse rotation (or from reverse to forward) during torque control under Real sensorless vector control.
- Check that the inverter capacity matches with the motor capacity.
- Check if a start command is given to the inverter while the motor is coasting.