Cause : Motor overload trip comes when the electronic thermal O/L relay function in the inverter detects motor overheat, which is caused by overload or reduced cooling capability during low-speed operation. When the cumulative heat value reaches 85% of the Pr.9 Electronic thermal O/L relay setting, pre-alarm (TH) is output. When the accumulated value reaches the specified value, the protection circuit is activated to stop the inverter output.
- Check the motor for the use under overload.
- Check that the setting of Pr.71 Applied motor for motor selection is correct.
- Check that the stall prevention operation setting is correct.
- Reduce the load.
- For a constant-torque motor, set the constant-torque motor in Pr.71.