Nidec & Control Techniques Commander C200, C300, NE200 & NE300 Drive
242
Apr 10, 2024 5:05 am
Cause : NV Media Card trip- option module installed is different between source drive and destination drive comes when the C.OPt trip indicates that parameter data is being transferred from the NV Media Card to the drive, but the option module category is different between the source and destination drives.
- This trip does not stop the data transfer, but is a warning that the data for the option module that is different will be set to the default values and not the values from the card.
- This trip also applies if a compare is performed between the data block on the card and the drive, and the option module fitted is different between the source and target.
- Ensure the correct option module is installed.
- Press the red reset button to acknowledge that the parameters for the option module installed will be at their
default values. - This trip can be suppressed by setting Pr 00 to 9666 and resetting the drive.
