Nidec & Control Techniques Commander C200, C300, NE200 & NE300 Drive
1
Posts
1
Users
0
Reactions
142
Views
Apr 10, 2024 5:05 am
Cause : NV Media Card data blocks are not compatible with the drive derivative comes when the C.Pr trip is initiated either at power-up or when the card is accessed, If Drive Derivative (11.028) or Product Typ (11.063) are different between the source and target drives. This trip can be reset and data can be transferred in either direction between the drive and the card.
- Use a different NV Media Card
- This trip can be suppressed by setting Pr 00 to 9666 and resetting the drive
- Choose a file compatible between the source and target drives, if sub-trip 2